以下UL PAG中的对保险管炸开的现象的判定指导: Y* \$ C3 ]% i, R& ~1 r- w
5.3.8-1 Bursting fuses b* M" U9 {! g# k
STANDARD IEC/UL 60950-1! d( ?) ?. h/ }4 P" W, u, ?3 `0 M
APPLICABILITY UL(C-UL) and IEC
! o4 g5 J/ n* _7 P# ~9 ](Sub)CLAUSE/ANNEX NUMBER: 5.3.8
8 E1 N' ?1 q9 t0 ^0 G8 `2 Q(Sub)CLAUSE/ANNEX HEADING: Compliance Criteria for Abnormal Operating and Fault Conditions
* {( y% V; n, L# ZOTHER RELEVANT (Sub)CLAUSES/ANNEXES
- r0 p# g4 T# L% Q5 x(as Applicable):
# y* U! g3 d) z0 j4 U H' p2.7.3, 5.3.6, 5.3.8.1, 5.3.8.2
; D5 @1 n% \/ Z5 D+ Z7 ]7 PDESCRIPTION OF ISSUE:
2 H$ S8 C+ Q0 _( @) _" x1 MType of Issue: Technical; e0 r$ K1 @' B6 E6 _
During fault testing in the Primary circuits of switch mode power supplies (SMPS) and other ITE,1 d; s8 B8 I1 h3 r2 b0 K
sometimes a fuse that provides supplementary (non-branch circuit) overcurrent protection and
5 q/ x' l2 O- m# C2 Dthat complies with either IEC 60127 or UL 248-14 will burst while clearing the circuit
. p/ l6 p0 X8 m( |, {2 E T$ Q) S& nIs this an acceptable result and termination of the test?
/ D# ^- Q$ I; pAPPLICATION GUIDELINE:9 N( I% o8 r! L1 c2 ?
A fuse that bursts is not an acceptable result and termination of a test. If a fuse bursts during
' c, i6 b+ s$ Tfault testing per sub-clause 5.3, it does not have adequate breaking (rupturing) capacity.
3 t. [) f- W4 g6 [/ gTherefore, such a fuse should be replaced by the manufacturer with another fuse having high
# ^3 H9 l! D# n& F! {: Dbreaking capacity. This consideration applies to fuses complying with both IEC 60127 and UL" i% o; |0 Y! P+ D: C) @+ ?
248-14.5 A3 c' ?3 T3 {
Placement of heat shrink or similar tubing over the fuse assembly is not a suitable solution to
) V: B/ b" t% J* \' [9 r& b- h" Rwholly mitigate potential hazards associated with a bursting fuse. |
|