没错,接地电阻测试时大家都默认可以不包括电源线的,那是认为三根线(L、N、G)阻值一样大,在这种失效模式下阻值过大其实没有关系。测试仪器其实是带校正功能的,直接短路两根绿色的线归零就去掉了测试设备的阻值,大家无需担心测试方法的问题。
c$ I7 W: b5 p) u$ M( U) |: L* M* W! O/ a- I
但是这根电源线很蹊跷,用电桥法测试三根电线确实也是毫欧级,但是带载25A测试达到0.178欧,而L和N线带载25A却达不到这个阻值,你认为这根线的问题在哪里? ; P7 J' L! q! K+ |
( N. a6 {$ _ F6 Y$ }1 f7 H
标准也是有明确从插脚算起来的: , J- l1 ?# t" [( i& k
65.1 The resistance of the grounding path between any metal part that is required to be grounded (see
) L, J6 ]7 A1 h2 Q35.1.1) and the equipment grounding terminal or lead, or the point of attachment of the wiring system, or 7 ]0 A6 g- s# Q7 s7 T8 b. J, n& q: z
| the grounding blade of an attachment plug | , shall be no more than 0.1 ohm. + l9 b$ N9 Q, u
/ c1 p% m0 i0 C5 ^; O当然标准也在变,不一定从插头算起(UL1573):
8 [! X8 x" ]% X# W m, u36.4 When an indicating device of the type described in 36.3 does not indicate continuity of the grounding circuit, an alternating current or a direct current of at least 25 amperes from a power supply of not more than 12 volts is to be passed | from the point of connection of the equipment grounding means to a point |
| in the grounding circuit and the points |
. The resistance in ohms is then calculated by dividing the drop in potential (in volts) by the current (in amperes). The resistance shall not exceed 0.1 ohm. . Z1 Y0 D/ ^- d/ a7 p9 c
' F; V5 `* f6 \7 Q7 x9 D
UL153:
6 Q& F! r+ t- m4 [+ _136.2 Test method $ B0 Q* \, i" I+ v
136.2.1 The impedance between the point of connection of the equipment-grounding means and any other accessible metal part required to be grounded, shall be determined by applying a current of 25 amperes – derived from a 60 hertz source with a no-load voltage not exceeding 6 volts – | between the grounding connection and the metal part in question | . The resulting impedance is calculated by dividing the value of the measured voltage by the applied current (25 A).
4 G7 f' m/ f! S3 Z$ P2 v4 a4 |$ U6 ` e, c: f8 P$ d" M
大家考虑一下,为什么厂家要把地线做成与L和N电阻不一样?. N, _, V3 @4 W( C7 Q# J6 g