4. IEC 60335-1中什么是电子开关?1 V6 }5 z' U8 ~4 c3 T0 e' W+ i
Note:
2 [/ m- t$ L. J$ x$ w3 A4.1 60335-1中提到电子开关涉及的测试最主要就是19.11.4, 当然这个要和off position (3.8.2)一起考虑才有意义。
- j' w9 c2 L+ ?& {4 l. q0 j5 r- u8 [4.2 单纯地看待电子开关的话,请参看61058-1 table 15会很清楚:SSD without electrical contacts, SSD with serial contacts, SSD with parrel contacts, SSD with serial and parrllel contacts, 电子开关可以是半导体元件通断电实现off position, 或者是控制机械触点实现(例如继电器)9 q9 w4 F* u4 W. g# X/ o, G* A, \
4.3 24.1.3和Annex H也得看看。# c# S( K9 l% V; b+ m
! y$ {% p, M( C N
5. 关于IEC60335-1 cl 16关于泄漏电流加倍的讨论。
/ \- e" `, {7 y0 d. P" o; I1 S$ tNote: 这个问题在IEC TC 61 Chairman D.R.Johns写的IEC 60335 interpretation 里面有比较清晰的解释.
, u) u5 G; S3 B3 v( {* cIf the appliance is functionally switched off by a single-pole disconnection, then one end is left 7 L: M1 P+ r8 O- u5 Q# {) E' \" E
connected to the supply since the appliance is only functionally off. The leakage current
% e2 M; L0 O- T6 x8 }$ A' Cdistribution in the functionally off position can be as shown in figure A (格式问题,图贴不上来) and the nett leakage current will be Ix, where Ix is the leakage current per unit length of the insulation.
! P% i; M& T' K: Z; @# t8 s- hWhen the appliance is tested according to the method detailed in 16.2, the leakage current distribution will be as shown in figure A (格式问题,图贴不上来)and the nett leakage current will be Ix.
. i$ Y& X2 |- a6 c) T: E6 t* w6 _ z9 z0 @' E& `& q
When the appliance is on the leakage current distribution will be as shown in figure B (格式问题,图贴不上来)and the nett leakage current will be Ix/2 (since the appliance neutral is normally at or near earth potential).
) E o: f4 v; x- j5 B! ^2 O- ~/ p
- i% E" o% X4 W, m% m+ pIf the appliance is switched off by an all pole disconnection switch or by withdrawal of a plug 0 w, Y, u! a* Y9 }3 H& z2 M4 f
then one end is not left connected to the supply when the appliance is off and the leakage 9 ?1 {5 S# N' s# R& T" e
current in the off position will be zero. The leakage current value measured during the test of
( `+ K. O- ^7 N9 W' b9 e16.2 will be twice the mean value experienced by the insulation in practice.
- N1 s; c: K t2 z. `9 y
, l8 h" h0 P8 ?3 L, ^It is therefore, permissible to double the limit and still achieve the same level of safety as in the case where the appliance is switched off by a single pole disconnection switch. |
|