IEC 60598-1:2008 第5章中的要求& g; w9 N3 j/ _# b% ^0 `
Table 5.1 – Supply cords! i- ~. E' [4 e2 w' z0 G; d: ~
Luminaire Rubber PVC
6 G+ h3 Q' q7 p) W) cOrdinary class I luminaires 60245 IEC 89 60227 IEC 52
9 o0 q- ^6 p! Q P& b+ DOrdinary class II luminaires 60245 IEC 53 60227 IEC 52
& R5 ]+ I- w, ?7 H s4 pLuminaires which are other than ordinary 60245 IEC 57 –1 t: p' R" k; h; A! U/ x' [
Portable rough service luminaires 60245 IEC 66 –
9 ~9 `% @- y# g! f4 K7 C4 Y E
: Y3 Q* Z/ Y2 S. yTo provide adequate mechanical strength, the nominal cross-sectional area of the conductors7 W4 N1 j: H0 p: h* Z
shall be not less than:: e; o8 X3 X& @
– 0,75 mm2 for ordinary luminaires;
2 w0 O# A) R# ~9 ~& P– 1,0 mm2 for other luminaires.# @ c3 z; T. l' f8 o" k
If the luminaire is provided with a 10/16 A socket-outlet, the flexible conductor nominal crosssection area shall be at least 1,5 mm2. |
|