J哥,翻出你这个旧帖子了。我的1598资料还在整理当中,这部分信息我也会加进去。我查找了一下资料,把一些信息列在这里供你参考一下。/ _' {- Z0 g6 r& j- R* T* G
% s. T1 k; b- W. W6 O: O
那查看了NFPA 70中关于灯具的要求410章节,发现tap conductor就是固定连接到灯具内部端子的导线,用于连接到安装地点的电源出现盒的灯具导线,在这里姑且叫做“分流导线”。根据1598的要求,嵌入式灯具的tap conductor要求要有线管保护。但根据NFPA 70的要求来看,分流导线必须要有线管保护。
4 v( e8 e' X9 t& @5 q% F+ W% o8 M' _9 t
0 H9 ?3 f j/ F) _4 O下面是NFPA 70中关于tap conductor的摘录:9 Q! ]8 p( j) j0 _9 y' L& Z
410.117 Wiring.' J# l$ p% K" Z* N0 L- u1 u
(A) General. Conductors that have insulation suitable for the temperature encountered shall be used.0 ~- _/ H: x1 ~3 n) b
(B) Circuit Conductors. Branch-circuit conductors that have an insulation suitable for the temperature encountered
# e9 e5 ]- K7 lshall be permitted to terminate in the luminaire.( d5 _2 @; b( ]. t* p `
(C) Tap Conductors. Tap conductors of a type suitable for the temperature encountered shall be permitted to run from
+ y6 ]* n6 N; I! p& e: p _; ]the luminaire terminal connection to an outlet box placed at least 300 mm (1 ft) from the luminaire. Such tap conductors
" j/ V+ @( {7 Q {" _& `! tshall be in suitable raceway or Type AC or MC cable of at least 450 mm (18 in.) but not more than 1.8 m (6 ft) in length.) T. M! @# ?7 o& [
& O+ g: [+ [; r6 U( I5 z另外,灯具允许使用软线(即符合绝缘要求的用于给电器具供电的电源线)方式进行连接,根据1598,软线连接是不需要用导管保护的,而根据NFPA 70下面的条款,软线连接的灯具,软线的输入端必须有插头、连接器、符合要求的布线系统,或者不带插头、连接器时要带出现盒盖子+线管。. @7 a& W0 R% B/ i
- f" Y1 E6 R# ~. w# w+ w
下面是NFPA 70关于软线连接的灯具的部分要求:0 p3 N2 B3 v2 \- T: F
410.62 Cord-Connected Lampholders and Luminaires.0 Q; S! |: t' b0 ]/ h
(C) Electric-Discharge and LED Luminaires.
7 o" [4 Q# i& k% S8 u/ v* Y; i: k(1) Cord-Connected Installation. A luminaire or a listed assembly shall be permitted to be cord connected if the following conditions apply: X6 k8 |, Y/ t: T( ]: s1 D
(1) The luminaire is located directly below the outlet or busway./ L6 S% u% p; \, m" }6 E
(2) The flexible cord meets all the following:: H- t! L0 }0 i' f5 v
a. Is visible for its entire length outside the luminaire
) k5 A2 d" }# E; \! |b. Is not subject to strain or physical damage# K* O1 V: S; @
c. Is terminated in a grounding-type attachment plug cap or busway plug, or is a part of a listed assembly incorporating a manufactured wiring system connector in accordance with 604.6(C), or has a luminaire assembly with a strain relief and canopy having a maximum 152 mm (6 in.) long section of raceway for attachment to an outlet box above a suspended ceiling.
" u6 n# u% |- `那么比对灯具的软线和分流导线的区别,软线安装灯具中符合要求的软线不需要导管保护,但是软线一般带有插头,软线须含地线。而分流导线则不带插头,必须有线管保护,线管和分流导线连接到安装场所的电源出线盒上。
f. m' a+ Y& w+ Z3 a/ O" o |
评分
-
查看全部评分
|