对于电源线——有插头或者尾插的。' u- }1 u9 L( M& f/ U1 D7 F+ c; ]
各国的标准的规定:( y2 n( ?$ A' j" x- A" q6 c8 v
IEC 60884-1的17.1 The insulation resistance is measured with a d.c. voltage of approximately 500 V, the
. G5 ]/ d1 S6 j( _measurement being made 1 min after application of the voltage.
6 h1 ?6 v) T; i3 }% VThe insulation resistance shall be not less than 5 MΩ.$ G2 R5 R# D; _: N. s# x, Z
: D4 A, `) X1 {# zGB2099.1 的17.1条款,绝缘电阻5mΩ以上 {$ n [. \, U7 }' _% G3 H' K' e
" M6 U% n4 M5 l+ k) [JIS C 8303 的5.5 絶縁抵抗 絶縁抵抗は,7.6によって試験したとき,開閉試験前が100 MΩ以上,開閉試験後が5 MΩ以上でなければならない。' y& e3 n) m/ h
( N2 X' K, [" t- Z2 I H
UL 817 的89.1 The insulation resistance of a fitting shall not be less than 100 megohms between:。。。。。。& J! r x9 d2 b5 b' h8 z9 o x
: c9 ~/ Y; n. J& j! X) p9 iAS 3112的规定:' A" K' f$ i9 h8 r
2.13.2 Insulation resistance test
6 G2 A8 g, i; ~; B/ U6 [The insulation resistance of a plug shall be measured at a voltage of 500 V d.c. as follows:
- p+ P3 W- ~4 F* l* l。。。。。。
( ^. C, q$ L/ q/ xThe measured insulation resistance shall be not less than 5 MΩ. |
|