许多标准都提到等电位保护连接导体测试(protective bonding test)时,测试电流值应该为设备过电流保护设备额定值的2倍。
8 J$ A6 \) S- Z为什么是2倍?还请高人指点。。。。谢谢!!
: ?6 @0 u4 V# |1 M9 ]0 h. c5 ?; P u8 i( |. [: @5 A y+ j0 ]& [
如下摘自IEC60950-1:2005
" ?0 n+ r. {* R+ o* oThe test current, duration of the test and test results are as follows:. P6 S$ ]9 W- V2 y: P
a) For equipment powered from a MAINS SUPPLY, if the PROTECTIVE CURRENT RATING of the circuit under test (see 2.6.3.3) is 16 A or less, the test current is 200 % of the PROTECTIVE CURRENT RATING applied for 120 s. The resistance of the PROTECTIVE BONDING CONDUCTOR, calculated from the voltage drop, shall not exceed 0,1 Ω . After the test, the PROTECTIVE BONDING CONDUCTOR shall not be damaged.
4 G- [3 Q+ ?$ [& x7 Pb) For equipment powered from an AC MAINS SUPPLY, if the PROTECTIVE CURRENT RATING of the circuit under test exceeds 16 A, the test current is 200 % of the PROTECTIVE CURRENT RATING and the duration of the test is as shown in Table 2E.
6 z- {, o5 j' i# I* x |
|