本帖最后由 H-RH 于 2014-5-23 01:59 编辑 ' r$ g8 f. Z S/ v( E* P
0 S* [' O5 i& |; ~% G; h+ n c2 o/ P笔者内文意思大致如下: "买了一部 8kW 发电机, 附带了一条伸延电线, 但这款电线违反了最新美国条例, 究竟这个产品是否有 UL 认证?" 8 h8 ?7 {; K: X5 y, j0 u
1 o0 [% D" c( f4 Q首先, 内文所指违反之条例是 NEC 445.20, 即 NFPA 70 之 Section 445.20! 很不幸, 笔者所指的 NFPA 70 Section 445.20 是 2014 版之新增, 安规网内之 2011 版是没有的!
" ]# @0 G1 y8 T上网找了半天, 445.20内文如下:
+ l7 a5 [2 p- }445.20 Ground-Fault Circuit Interrupter Protection for Receptacles on 15 kW or Smaller, Portable Generators. All 125-volt, single-phase, 15-and 20 ampere receptacle outlets, that are a part of a 15 kW or smaller, portable generator, either shall have ground fault circuit interrupter protection for personnel integral to the generator or receptacle, or shall not be available for use when the 125/250 volt locking-type receptacle is in use. If the generator does not have a 125/250 volt locking-type receptacle, this requirement shall not apply.
& K* f9 ~6 v7 {* { i" e由于笔者没有清楚说明是伸延电线什么不符合条例, 但本人估计是没有 GFCI (Ground Fault Circuit Interrupter) ' w0 e7 a: X) {2 C, R
* J# G, R% Z( p, t1 e
" B" X. c- P$ T( e" f! l5 {另有一个小插曲, 曾经有生产商上诉要把条文改成 : 8 q/ X( \* X2 m+ V
445.20 Ground-Fault Circuit Interrupter Protection for Receptacles on 15 kW or Smaller, Portable Generators. All 125-volt, single-phase, 15-and 20 ampere receptacle outlets, that are a part of a 15 kW or smaller, portable generator, either shall have ground fault circuit interrupter protection for personnel integral to the generator or receptacle, or shall not be available for use when the 125/250 volt locking-type receptacle is in use. If the generator does not have a 125/250 volt locking-type receptacle or was manufactured or remanufactured prior to January 1, 2015, this requirement shall not apply. n4 S! r' a. |- P; c: |
即在 Jan 01, 2015 前生产之发电机可以豁免, 但最终上诉被驳回! |