有没有哪位清楚SAA 插座 高压测试要求,对地线脚的高压测试是多少伏? t q7 e* ~# x$ Y8 [- e) K! G
The socket-outlet shall withstand, without failure, an a.c. voltage of the value indicated in Table 3.3 applied between the parts set out in Items (a) and (c) of Clause 3.14.2 for 1 min in each case. The socket-outlet shall further withstand, without failure, a voltage of 3500 V a.c. applied between the parts set out in Items (b) and (d) of Clause 3.14.2 for 1 min in each case. The socket-outlet shall be fitted with an appropriate plug during the test./ g( R- Y$ {; Q, C$ B
TABLE 3.3 TEST VOLTAGES FOR HIGH VOLTAGE TEST4 z8 H' B7 r* M$ u
Working voltage (r.m.s.) between parts (See Note) Testing voltage
% q$ k+ R! l! v( T ≤ 32 V 500 V 3 z9 U& h# _. U, w9 M8 f6 f
> 32 V ≤250 V 1 000 V
+ A/ D7 N T+ k/ Z. A>250 V ≤650 V 1 000 V + (2 ×working voltage) with a maximum of 2000 V 1 \) H7 r) v4 b& R
NOTE: For example, a socket-outlet for connection to a system operating at 415 V between phases and 240 V to earth, would require a test of 1000 + (2 × 415) V between live terminals but a test of only 1000 V between live parts and earth. , E" a$ N' E& A0 K6 E1 w% }
8 U# C7 g( T) v. M3.14.21 }2 {- q) |0 C, l& ^
d,Between live terminals of the socket-outlet and the earthing terminal (if any), with the live terminals of the plug being connected together. |
|