& O0 ]# A& x' p1 qThe socket-outlet shall withstand, without failure, an a.c. voltage of the value indicated in Table 3.3 applied between the parts set out in Items (a) and (c) of Clause 3.14.2 for 1 min in each case. The socket-outlet shall further withstand, without failure, a voltage of 3500 V a.c. applied between the parts set out in Items (b) and (d) of Clause 3.14.2 for 1 min in each case. The socket-outlet shall be fitted with an appropriate plug during the test.
: C: F% e. O) D, ?TABLE 3.3 TEST VOLTAGES FOR HIGH VOLTAGE TEST
h7 R- r: i0 I, H/ ?1 M& rWorking voltage (r.m.s.) between parts (See Note) Testing voltage
3 W2 ]- M6 {2 R- _4 }1 B ≤ 32 V 500 V
/ `/ O3 t8 F+ }3 K! U/ c( C# k > 32 V ≤250 V 1 000 V " K* N! I4 O$ X$ \
>250 V ≤650 V 1 000 V + (2 ×working voltage) with a maximum of 2000 V
, i8 N4 |3 a* X7 `- E4 B4 cNOTE: For example, a socket-outlet for connection to a system operating at 415 V between phases and 240 V to earth, would require a test of 1000 + (2 × 415) V between live terminals but a test of only 1000 V between live parts and earth.
; ?# a L1 M% Y( A( F9 [; P. G1 ~% |! Q' q. |2 R0 }6 x6 a
3.14.2 ~9 e$ o6 t% A& o/ f: w( o1 H5 p
d,Between live terminals of the socket-outlet and the earthing terminal (if any), with the live terminals of the plug being connected together. |
|