| DSH 1033
4 d6 M7 ~3 [* g, W8 ^5 d9 z: R& a! c& h; ?' [+ x1 W2 ]+ o( b
| Separation of welded contacts after short-circuit test
# |: f$ \2 q( A& f! y$ i | 9.3.4.2.3.j (60947-4-1) 8.3.2.1 (60947-1)
3 y5 Q7 o9 n; C7 ]7 {0 `& \ | 60947-1(ed.5) & 60947-4-1(ed.3)
: f& ]% S$ u0 c% I+ H |
& H- M7 o7 R: {# XCTL Decision Sheet - DSH 1033
8 r" e3 ]3 q! r3 w4 z(replaces PDSH 1033 on 2012-10-22 by CTL Chairman decision,
. _' d/ c+ Y* V; Awill be kept remaining until final decision by 50th CTL Plenary Meeting)% P1 ? o0 Y( y M
SC 17B/Publication IEC 60947-4-1 Edition 3.0 2009-09
. N( y% ?( Y7 d, H# YLow-voltage switchgear and controlgear –
2 Y: [0 \4 ?7 x9 JPart 4-1: Contactors and motor-starters – Electromechanical contactors and
5 T+ l5 V: L& o! U0 `" jmotor-starters
, _8 E3 T+ B$ vINTERPRETATION SHEET
( z' H+ }- b( [: } R2 UThis interpretation sheet has been prepared by IEC SC17B/WG2 on 2012-09-06
2 f0 `! V. y3 fThe text of this interpretation sheet is based on the following documents:3 Y- [* a8 Z& d W' N4 M" \6 k6 B
IEC 60947-4-1 ed 3: 20096 k! p9 i: m- q/ l. _ f9 r
___________$ g7 K% m9 J4 L+ K H7 ^/ U4 b( X$ W
Interpretation8 r# I, d( F3 H
In Clause:
3 c6 L2 ^6 y( S- f6 I! A6 t( T: l9.3.4.2.3 Results to be obtained
( q( w3 P q+ b0 C t# C) |The contactor, starter, or the combination starter, the combination switching device, the; S% X% |, K' |' ~
protected starter or the protected switching device, shall be considered to have passed the
; U5 ]" u7 h5 [4 A4 \8 stests at the prospective current "r" and, where applicable, the prospective current Iq, if the( C7 K+ W8 p8 o- K5 v) H! }
following conditions are met for the claimed type of co-ordination.
1 h3 c' N4 m8 y: n8 tType "2" co-ordination (all devices):5 x2 g, U, o/ N' a2 b
J No damage to the overload relay or other parts has occurred, except that welding of
# N. `% }4 X" G! gcontactor or starter contacts is permitted, if they are easily separated (e.g. by a
( G8 X% M" i6 J$ X, {screwdriver) without significant deformation, but no replacement of parts is permitted8 F& ]4 b8 s5 Z3 Y/ t
during the test, except that, in the case of fuse protection, all fuse-links shall be replaced.* Z: F& e9 G: e, {
In the case of welded contacts as described above, the functionality of the device shall9 z% W% u8 u% I' N. ?4 ?7 j, p
be verified by carrying out 10 operating cycles under the conditions of Table 8 for the
( d# t$ n5 G0 B4 ? zapplicable utilization category.% j& O0 h- q# |/ S3 O. O/ _
The text "if they are easily separated (e.g. by a screwdriver) without significant deformation"
3 c! u H# o! _shall be interpreted as follows:
' Q' G) F( {3 u, a9 E* k; l' ?"Easily separated" means a separation realised on site for example by:- C) {7 N, S7 d* }3 F" U
- Energizing the coil of the contactor
+ E# Y$ Q$ K- \# I& f8 `- Using a tool (eg. a screwdriver) for separating the welded contact or for moving an operating
. W3 t% M0 n0 N/ `+ jmeans.
; n# {! R( `8 D$ u/ v2 V, _It is also allowed to remove covers or housing of the contactor according to the instruction of' y! \+ R% m4 Z R x
the manufacturer." P* s( A/ `7 L$ a( u
"Without significant deformation" means a deformation without impairing the insulation of the$ I, m% ^4 }. N( _" ?
contactor (see d) and i) of this Clause) and successfully performing the 10 operation cycle: k8 e9 ^% E0 M- U
specified in the last paragraph of J.) S* c; G+ K9 }' i0 D0 g
* p. B) j; t3 U1 N+ j+ `- h ^" I( g" }# o! w
|