| New glow wire test requirments (650 C) for parts close to contacts
. A% m( ?/ D% T' |' ~ | Clause 7.1.1.1 of IEC 60947-1 Clause 21.1.5 of IEC 61058-1/ @) D' D( l. ~& Y; s
| 61058-1(ed.3) & 60947-1(ed.4)( }: n; K8 I: m2 | K$ S v* M
|
- m M: C1 L& P Q7 g& [Standard(s)- (year and edition):( {" _! G$ ?( u/ x/ d5 F& w) ?
IEC 60947-1:2004 IEC 61058-1:2000% L. r- U0 ]: g" |4 S. P. L
Sub clause(s):5 j ^$ o8 A5 c# P* Z2 O& O
Clause 7.1.1.1 of IEC 60947-1 Clause 21.1.5 of IEC 61058-1
! h1 ]% Y; |7 }; j) lSheet n°:& z, f5 L. r: S! e7 I
DSH 593; j, f) {. A% z
Subject:0 J& G% ^% Y# X) c |$ i
New glow wire test requirements (650 °C) for parts close to contacts! i1 b" b3 S9 g: C
Key words:! T$ p$ `* ~$ b5 C: B- r, U
- glow wire
, K. L; z+ \) ^6 s& u7 {9 X$ lDecision approved by the 44th CTL meeting 2007" Z3 ?# ?0 o3 z- M: `0 Z# [
Question:4 S e+ |0 c2 }5 W5 u# T0 X
Due to the new requirements of 60947-1:2004, parts close to contacts are subject to glow wire test performed at temperature of 650 °C. Is a glow wire test necessary for the green part (figure 1) or isn’t a glow wire test required for this part?, a2 J: _3 A( K5 Q3 R
Decision:
W, ~& N# W7 r0 P G& k3 D r) mAlthough the green part (figure 1) of this switch is mechanically separated from the contact element, the glow wire test should be done with 650 °C. During normal operation, the switching element and the contact element are mounted together. Due to this fact and the relatively large amount of material, a test should be done.4 f1 | U4 ?$ Z% |( X% U4 I. I