head0819 发表于 2015-12-25 13:08 ( {! f4 Q& E( G
我们还是参考一下UL62 Flexible Cords and Cables
/ e/ K: t7 g8 j" a3 V0 c其实所有这些所谓的白色/灰色是零线的要求要回到:NFPA 70 第200.6节要求:/ q+ U1 H4 m$ E; h
200.6 Means of Identifying Grounded Conductors.5 N$ }2 _1 O4 I! w5 a6 x7 \; Y
(A) Sizes 6 AWG or Smaller. An insulated grounded conductor6 q. g/ k1 B; ^8 h8 J3 Q4 C
of 6 AWG or smaller shall be identified by one of
, l% k8 H% {% k5 f; Q' [/ Xthe following means: N) S' ~" m; n1 f7 U
(1) A continuous white outer finish.
( ]" G, |1 v% R! {, C' G(2) A continuous gray outer finish.8 F$ Y9 l2 k8 v5 q9 \6 x
(3) Three continuous white or gray stripes along the conductor’s
, n: z C# ~3 b6 u8 l7 ]8 h4 U _2 @4 Fentire length on other than green insulation.
1 y6 N1 {5 s( D8 G9 u, G w(4) Wires that have their outer covering finished to show a3 O0 Z2 C. }9 E' k& y4 {
white or gray color but have colored tracer threads in
. i, m7 Z5 i1 K9 C' athe braid identifying the source of manufacture shall be# X0 O3 O2 S& C6 j
considered as meeting the provisions of this section.
$ k: j- j. S, ^* o6 X' Y4 j" `(5) The grounded conductor of a mineral-insulated, metalsheathed
4 l% b1 H. e0 ]0 Q( }. qcable (Type MI) shall be identified at the time of
' j z7 ]5 R7 r) T7 Pinstallation by distinctive marking at its terminations.
# \, v+ i' q' i# O(6) A single-conductor, sunlight-resistant, outdoor-rated( L* i; k# C- q0 ^$ l
cable used as a grounded conductor in photovoltaic+ E& t/ T" S6 g* x4 W
power systems, as permitted by 690.31, shall be identified
2 ^3 k( w) |4 k0 K% S$ L" Kat the time of installation by distinctive white0 @; \- z* d( [- ?- z2 J
marking at all terminations.
2 d, O4 v1 f G: y; T, z(7) Fixture wire shall comply with the requirements for* n0 ~8 B5 ?: s' D
grounded conductor identification as specified in 402.8.
8 G1 H9 ?$ u% a( M(8) For aerial cable, the identification shall be as above, or
/ F3 X: {- }5 J3 N5 \/ Y, P8 ?$ zby means of a ridge located on the exterior of the cable
0 o6 A; t9 q) t4 m- Bso as to identify it.) Z v4 q, K T* a* A
# N1 ?/ f( r- N$ X `" B
(B) Sizes 4 AWG or Larger. An insulated grounded conductor
) U1 d9 |+ x2 Z, s4 AWG or larger shall be identified by one of the
& ?0 v6 C; Z8 S9 Hfollowing means:
+ G0 h6 t. \. _9 t2 i# q(1) A continuous white outer finish.
$ s' \5 f/ F! Q6 r(2) A continuous gray outer finish.
: I, W3 O8 q! i9 V+ ^1 M$ |(3) Three continuous white or gray stripes along the conductor’s6 a `* c$ _! g2 c" |
entire length on other than green insulation.- A, {1 o4 d" e; i6 o) y
(4) At the time of installation, by a distinctive white or/ y$ D9 d6 B: r) i( f+ D
gray marking at its terminations. This marking shall% U S' _: r; k
encircle the conductor or insulation.
/ g4 g, p' g- d6 \5 b+ B/ H(C) Flexible Cords. An insulated conductor that is intended2 {% Y- b( o4 o) D9 f2 k# `
for use as a grounded conductor, where contained
! ?2 S% {% @4 W5 B" O3 ^+ vwithin a flexible cord, shall be identified by a white or gray& c D+ u* A" Y. u/ p
outer finish or by methods permitted by 400.22.
- g! A0 H6 }- o5 y0 T(D) Grounded Conductors of Different Systems. Where/ u7 o4 C3 I, I: S7 `" X2 \' Z% ^/ Z
grounded conductors of different systems are installed in
& n, g6 }/ B7 J5 w, L4 H! r. w$ Uthe same raceway, cable, box, auxiliary gutter, or other type R7 x& n1 Q) F% ]1 L/ }) _
of enclosure, each grounded conductor shall be identified1 f! Z. G; s: k+ h
by system. Identification that distinguishes each system' K; d3 F% u( G, h& Y' C8 T$ u
grounded conductor shall be permitted by one of the following" Y% s! Q7 L% H0 g
means:
: I# \. L6 b1 [3 X0 t* L) @2 {(1) One system grounded conductor shall have an outer* z, H0 V4 M+ @
covering conforming to 200.6(A) or (B). p1 O( K4 u b0 ]
(2) The grounded conductor(s) of other systems shall have+ b1 |4 g. T f
a different outer covering conforming to 200.6(A) or
7 A$ q) p" r% k" n% k200.6(B) or by an outer covering of white or gray with
& W( n) \3 H# \2 n) Ka readily distinguishable colored stripe other than green
( U% [- G/ {! y. srunning along the insulation.: B& ?1 g/ j8 Q* A. M7 t
(3) Other and different means of identification as allowed, z8 ]/ E/ l0 G7 z9 y C$ c+ X
by 200.6(A) or (B) that will distinguish each system/ Z5 {; i' o7 e/ P; n$ j6 l
grounded conductor./ M9 U2 X \+ y6 I! f! H
The means of identification shall be documented in a6 X4 Y" p0 I& q, R2 a |: b
manner that is readily available or shall be permanently9 @3 @$ q5 x+ M# M( [
posted where the conductors of different systems originate.4 R, a6 J/ i$ w
(E) Grounded Conductors of Multiconductor Cables. The# }/ z& r8 x x; l( M. P7 I
insulated grounded conductors in a multiconductor cable shall
3 m' y$ X) B/ @be identified by a continuous white or gray outer finish or by
' W: I3 N4 K8 E- C* mthree continuous white or gray stripes on other than green5 P4 _. P# G( N
insulation along its entire length. Multiconductor flat cable. [2 ^8 s3 m+ Y8 F( ~( D/ y! n
4 AWG or larger shall be permitted to employ an external9 f1 |8 X& H: _7 H& U. ]) F+ e
ridge on the grounded conductor.8 d( k- Q2 A* i- y5 p( q( q
Exception No. 1: Where the conditions of maintenance and/ g$ D" N& Y9 {* f' J$ X
supervision ensure that only qualified persons service the installation,. N8 j0 E6 |! X: M7 X# y
grounded conductors in multiconductor cables shall
$ ]+ t+ g- K4 @be permitted to be permanently identified at their terminations* L$ P" O' t2 G% _7 U+ y$ m' b3 g
at the time of installation by a distinctive white marking or) h& D# f5 K, U2 |
other equally effective means.( }. V* ]% S: q+ u
Exception No. 2: The grounded conductor of a multiconductor$ h3 W( O7 ~) G+ f7 g) a. ]
varnished-cloth-insulated cable shall be permitted to be
# ?( Y. _0 v, `# y/ r1 G: }+ m& e& B( \1 k
identified at its terminations at the time of installation by a/ |. C% n9 d* G" w3 t
distinctive white marking or other equally effective means.. L% c' E' S3 T- _# u8 x! H
Informational Note: The color gray may have been used in: @' \* C2 N2 S
the past as an ungrounded conductor. Care should be taken8 } [- S t8 Z: D6 @8 o
when working on existing systems.3 V4 a) b' u, G1 v/ O( g7 p
1 |: v% A7 R s9 y
9 D ~5 h$ x) o: _ A有兴趣的可以看看。Grounded就是说的Neutral。你所列的UL62要求就是200.6 (C)要求。 |
|