* [8 q+ q+ z2 e% ]+ }- ^( u | Clause 7.1.1.1 of IEC 60947-1 Clause 21.1.5 of IEC 61058-1
1 F) [" u1 r( J! p7 {! I& ~+ O | 61058-1(ed.3) & 60947-1(ed.4)
- T7 Z1 W! Y* H |
- L$ S" L4 ~$ f0 P2 i/ b/ \* rStandard(s)- (year and edition):
7 N" C' w& N" Z, @9 t% YIEC 60947-1:2004 IEC 61058-1:2000
) n7 l7 \! S& F% y) M: t6 rSub clause(s):
+ g2 V2 f5 w! k2 [Clause 7.1.1.1 of IEC 60947-1 Clause 21.1.5 of IEC 61058-1- V) Q: H$ n7 P7 A9 y: N- T
Sheet n°:: Y9 ?$ M* F* G+ n3 L
DSH 593
5 x' S0 j! F" k% sSubject:" D! l9 N# |# `0 e" w
New glow wire test requirements (650 °C) for parts close to contacts
% _4 H4 |- d5 D; n& c) @' GKey words:
2 l, n$ P9 Q( Q; a' m- R' z! o! G$ _- glow wire
6 r, e" f6 Z% m8 d# ADecision approved by the 44th CTL meeting 2007. G/ z- ^5 }- S6 `9 b
Question:1 }# o7 G7 r( b/ ^! l7 ?1 ^2 P
Due to the new requirements of 60947-1:2004, parts close to contacts are subject to glow wire test performed at temperature of 650 °C. Is a glow wire test necessary for the green part (figure 1) or isn’t a glow wire test required for this part? Z9 k/ x5 @ |6 l* h/ @0 b
Decision:& |9 q5 `4 g. o( I- R3 t
Although the green part (figure 1) of this switch is mechanically separated from the contact element, the glow wire test should be done with 650 °C. During normal operation, the switching element and the contact element are mounted together. Due to this fact and the relatively large amount of material, a test should be done.4 S: N8 X( [* g5 k/ X, J& V! H
) J" a$ t2 c# y" `5 u* p) J E' t* d/ y
|