8 V C, \' C. ?# [3 i | Impulse voltage test T2.33 h8 y4 s, y: R# ?
| Note 1 of table 5
3 V0 x& P& G7 S1 X | 61543(ed.1)% _& y# n- ?2 ?" o4 a6 t( q9 y. Z9 O* T
|
' a- |' u( V7 H) jQuestion:
* Z' P. w- R z; @In the application of IEC 61543 it was noted by various testing laboratories that note 1 of table 5 (referring to the impulse voltage test T2.3 for immunity to conducted unidirectional transients of the micro-/millisecond time scale) does not give information about the number and the polarity of the impulses to be given.
( {5 |( k( w- ^; f5 M% `0 aDecision:% v, x J4 w* \) f |7 ]5 C
The mentioned note 1 shall be interpreted by replacing the first line by:5 p! P, _2 B6 [/ n3 H( o
“This test shall be carried out with the RCD, in the closed position. A total of five positive and five negative pulses (for each phase angle) shall be applied synchronised to the voltage phase at the zero-crossing (0°) and the peak value of the a.c. voltage wave (90° and 270°), for each of the following tests:
( L# v2 \& u% K2 z L- between the metal support....”, E$ f2 R6 ~& b7 R2 ~, Q$ a
& h/ f% C; ]# ^5 M7 T
' v9 l0 n) a( n" T8 P0 h: r0 z |