有没有哪位清楚SAA 插座 高压测试要求,The socket-outlet shall withstand, without failure, an a.c. voltage of the value indicated in Table 3.3 applied between the parts set out in Items (a) and (c) of Clause 3.14.2 for 1 min in each case. The socket-outlet shall further withstand, without failure, a voltage of 3500 V a.c. applied between the parts set out in Items (b) and (d) of Clause 3.14.2 for 1 min in each case. The socket-outlet shall be fitted with an appropriate plug during the test.
/ Y4 {/ ~- Q* H& z: k TABLE 3.3 TEST VOLTAGES FOR HIGH VOLTAGE TEST
0 A( j) a( ]6 J: ], l Working voltage (r.m.s.) between parts (See Note) Testing voltage
- d3 t# J+ D( n z3 `" D6 | ≤ 32 V 500 V
& h; G8 [: H8 n > 32 V ≤250 V 1 000 V " I! h+ D) @0 Y
>250 V ≤650 V 1 000 V + (2 ×working voltage) with a maximum of 2000 V
* c' r6 Q* c7 P; Z& d$ R! ONOTE: For example, a socket-outlet for connection to a system operating at 415 V between phases and 240 V to earth, would require a test of 1000 + (2 × 415) V between live terminals but a test of only 1000 V between live parts and earth.
8 K. d. M. F; c$ {9 @/ u/ P: k& N5 ~5 c! ~ b6 {
3.14.2
4 u8 t/ G( Q4 P5 g) _d,Between live terminals of the socket-outlet and the earthing terminal (if any), with the live terminals of the plug being connected together. |
|