4.10.1 For metal encased class II luminaires, contact between:
/ |7 X4 Z3 B" Z% ^4 ?: r– mounting surfaces and parts with basic insulation only,- U' m5 }2 P1 N6 l4 F+ S% `
– accessible metal parts and basic insulation,) h/ b! ]; z) t1 X8 l1 _$ U
shall be effectively prevented.# M+ W& `# l! ] {1 n, u
NOTE 1 This requirement does not exclude the use of bare conductors if adequate protection is provided.( m" J" C9 Z6 T5 X/ C# H# n
This wiring includes internal and external wiring of the luminaire, and fixed wiring of the' f* ~. p9 j' T2 h" q7 a6 n
installation.1 o/ t0 v8 N0 _. l" f5 M
Class II fixed luminaires shall be so designed that the required degree of protection against
' c8 h" K& N' z V2 l" }- L7 ?% C) Relectric shock is not impaired as a result of the installation of the luminaire, for example by) H2 S9 v& K) t
contact with metal conduits or metal sheaths of cables.& e) G$ k4 r+ u* @
Capacitors shall not be connected between live parts and the body of metal encased class II
7 P" b e* d9 y* b5 ?9 Tluminaires, with the exception of interference suppression capacitors and switches meeting the% I5 d" t$ s3 U! F' h
requirements of 4.8./ l4 g& {; E8 t1 d
The interference suppression capacitors shall comply with the requirements of IEC 60384-141 m1 e z2 V$ r; ]% d7 }
and the method of their connection shall be in accordance with 8.6 of IEC 60065.
1 k z7 \1 K ^* M+ bNOTE 2 Contact between accessible metal parts and the basic insulation of internal wiring may be prevented by
- g6 L. \, Y9 j! Zsleeves or similar parts which comply with the requirements for supplementary insulation.6 F1 c' W! ]& Z* k5 o. t
Compliance is checked by inspection.- e9 V3 G, f( |