2 d% z5 x* o' W据本人理解, 完成 “insert” and “withdrawn” test 后, 不应用经过测试后之 ISOD plug 去做 earth resistance test (BS 1363-2, 10.2.1B), 应用 “standard rewirable plug used prior to the test”, 即 “three different makes of rewirable plugs”
. }/ b+ B* w: {8 ]: g( J- w6 F& a. G9 ^7 {0 E4 N+ X, H
12.9.5.2 Compliance shall be checked by the following: M; v" x! l, _9 [ d
6 ^" i" ^. B Y p$ X# {
Using a selection of three different makes of rewireable plugs conforming to this standard and three different makes of unswitched socket-outlets conforming to BS 1363-2, selected to represent different earth contact designs, the earth resistance between the earthing plug pin and earthing socket contact of the socket-outlets shall be established in accordance with BS 1363-2, 10.2.1b).
( O9 B7 |1 n! |! d- b& Q8 N' a5 N+ ?9 y' _6 d9 z% N2 Z
All socket outlet shall be of the type where the earth pin or ISOD of a plug inserted into the socket-outlet operates the shutter mechanism. ......1 E2 _3 w3 k T0 _