海之未央 发表于 2012-11-27 15:44

62109-2对于隔离型逆变器的要求

对于IEC62109-2好像对隔离有要求,如4.4.4.15.2 Fault-tolerance of automatic disconnecting means,里面明确写了be such that with a single fault applied to the disconnection means or to any other location in the inverter, at least basic insulation or simple separation is maintained between the PV array and the mains when the disconnecting means is intended to be in the open state.

那么意味着任意单点故障的时候我们逆变器依然要满足基本绝缘才行,,,,,那么对于内置隔离变压器的隔离型逆变器,,,该怎样来满足这个要求呢? 是否在AC输出这边一定要有relay?

houfengp83 发表于 2012-12-1 00:26

隔离变压器已经在PV与电网之间起到基本绝缘的隔离,自然可以不要继电器,相反的没有隔离变压器的则需要二级继电器来实现基本绝缘

vaimar21 发表于 2012-12-10 14:41

houfengp83 发表于 2012-12-1 00:26 static/image/common/back.gif
隔离变压器已经在PV与电网之间起到基本绝缘的隔离,自然可以不要继电器,相反的没有隔离变压器的则需要二级 ...

短路变压器主次级算不算单一故障?

戏尘 发表于 2012-12-10 19:37

vaimar21 发表于 2012-12-10 14:41 static/image/common/back.gif
短路变压器主次级算不算单一故障?

肯定是单一故障啊,一般情况我们短次级。

vaimar21 发表于 2012-12-11 17:26

戏尘 发表于 2012-12-10 19:37 static/image/common/back.gif
肯定是单一故障啊,一般情况我们短次级。

主跟次短的单一故障下,隔离逆变器算是没有基本绝缘了吧?

海之未央 发表于 2012-12-12 17:18

houfengp83 发表于 2012-12-1 00:26 static/image/common/back.gif
隔离变压器已经在PV与电网之间起到基本绝缘的隔离,自然可以不要继电器,相反的没有隔离变压器的则需要二级 ...

我也是这么理解的,即使短路也是初级和次级分别短。。。。但貌似某机构签证官上周跟我说即使有隔离变压器也还是要满足62109-2的要求,也就是说单一故障情况下也一定要r机械隔离,所以必须要relay。

海之未央 发表于 2012-12-12 17:19

戏尘 发表于 2012-12-10 19:37 static/image/common/back.gif
肯定是单一故障啊,一般情况我们短次级。

单点故障应该不包括初次级的短路吧? 一般都是初级或者次级分别短撒

戏尘 发表于 2012-12-14 10:52

海之未央 发表于 2012-12-12 17:19 static/image/common/back.gif
单点故障应该不包括初次级的短路吧? 一般都是初级或者次级分别短撒

怎么不包括初次级的短路呢?一般我们短辅助电源部分啊 光耦 等

海之未央 发表于 2012-12-14 11:06

戏尘 发表于 2012-12-14 10:52 static/image/common/back.gif
怎么不包括初次级的短路呢?一般我们短辅助电源部分啊 光耦 等

光藕属绝缘于有认证的隔离器件,,,一般对于有认证的功能是不需要评估的吧? 单点故障不是主要针对无认证的功能和器件么?

清水白菜 发表于 2012-12-14 13:21

海之未央 发表于 2012-12-12 17:19 static/image/common/back.gif
单点故障应该不包括初次级的短路吧? 一般都是初级或者次级分别短撒

要是內部有帶隔離型的Inverter, 初次級不做Single fault評估,需滿足相關隔離絕緣距離來滿足要求.。
页: [1] 2
查看完整版本: 62109-2对于隔离型逆变器的要求