标题: 请教:什么是 Safe installation fixed luminaires? [打印本页] 作者: yangxuh 时间: 2008-6-6 10:30 标题: 请教:什么是 Safe installation fixed luminaires? 如题,望不吝赐教!作者: yangxuh 时间: 2008-6-6 15:08
在IEC 60598-1, Cl. 4.10.1作者: wwnw_007 时间: 2008-6-6 15:25
4.10.1 For metal encased class II luminaires, contact between:$ ?, h- f$ k7 X+ F: [+ X* g
– mounting surfaces and parts with basic insulation only, 7 l! b& K* Z4 D– accessible metal parts and basic insulation,7 o0 f) ` l5 F/ F
shall be effectively prevented.. y0 p" {- I' k) Z0 Q$ h1 }- m
NOTE 1 This requirement does not exclude the use of bare conductors if adequate protection is provided.% [0 D% C$ [5 P+ F2 f& k" \
This wiring includes internal and external wiring of the luminaire, and fixed wiring of the9 l% T7 n: l) f' V2 C1 o n, a
installation. 8 R0 _. N+ `; ^% U4 YClass II fixed luminaires shall be so designed that the required degree of protection against 3 y* r7 B" I8 n! m/ }; W7 F5 Pelectric shock is not impaired as a result of the installation of the luminaire, for example by . r4 X8 H2 N/ b n* @contact with metal conduits or metal sheaths of cables.! G( k1 L8 V, ~" R* y
Capacitors shall not be connected between live parts and the body of metal encased class II ; X. Y( D, X" C$ v3 r9 B {luminaires, with the exception of interference suppression capacitors and switches meeting the ) a0 m4 h* a6 Q5 krequirements of 4.8.4 o5 F: a) a: C* d0 q6 ?/ s
The interference suppression capacitors shall comply with the requirements of IEC 60384-14! @% o& W6 S% s! R+ L) u
and the method of their connection shall be in accordance with 8.6 of IEC 60065. B. E4 P. N* ~: D/ y3 s0 F
NOTE 2 Contact between accessible metal parts and the basic insulation of internal wiring may be prevented by$ x( Q1 Y: c$ h4 N! ^4 ]
sleeves or similar parts which comply with the requirements for supplementary insulation. ( { q( @$ ]6 f5 s: b. c) cCompliance is checked by inspection. & N% d8 l) [; f以上是IEC 60598-1的4.10.1部分,没有你描述的词语!是哪个版本的? [s:90] [s:90]